SN series panel to SN subpanel question

Status
Not open for further replies.
I have a new SN series 200 amp panel and need to install a subpanel.

I wanted a matching one so everything would be fully interchangeable and got another SN 200 panel.

The supply house sold me 4-0/4-0/4-0/2-0 SER to interconnect the two panels.

The main panel came with the 200A breaker

The subpanel came with the lugs.

Now I need either lugs or a breaker to add to the main panel that can handle this size wire.

I found ECLK2225 but it looks like it doesn't handle that size.

How can I make this work?

Thank you!
 
What size wire will the lugs take?

Is the ser aluminum? Maybe the lugs aren't rated for aluminum

How far is the run between the two panels?

What size wire will the lugs on the MLO panel take
 
Last edited:
Status
Not open for further replies.
Top