BAHTAH

Senior Member
Location
United States
2005 NEC 426.28 Calls out ground fault protection for fixed outdoor snow-melt. We are figuring an installation for roof deicing cables. I am trying to find the code article (if any) that addresses this GF protection with respect to the milli-amp level. I seem to remember that for snow melt a 30ma GFI could be used but do not see anything in 426 that states a milli-amp level. Does anyone know where in the code this info can be found?
 

iwire

Moderator
Staff member
Location
Massachusetts
There is a definition of "ground-fault protection of equipment" in Article 100.

It looks to me like the manufacturer of the product you are using could tell you what current level protection will meet the requirements.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
You're looking for the attached verbage to 426.28. There is commentary in th NECH that explains GFEP vs GFCI. Both are important, for different reasons.
 

pgordon

Senior Member
Location
Maine
Occupation
Electrician
What the heck are you guys talkin about ? I just quoted 3 jobs with regular gfci breakers.
 

jmsbrush

Senior Member
Location
Central Florida
Section 426.28 requires ground fault protection of equipment for fixed outdoor electric deicing and snow-melting equipment. Rather that protecting the entire branch circuit, The ground fault protection requirement is focused on protecting the equipment itself
 

celtic

Senior Member
Location
NJ
Here is the mysterious verbage from the NECH:
Section 426.28 was revised for the 1999 Code. Section 426.28 states that ground-fault protection of equipment is to be provided for fixed outdoor electric deicing and snow-melting equipment. Rather than protecting the entire branch circuit, the ground-fault protection requirement is focused on protecting just the equipment itself. This affords the manufacturer and the user an option of providing both circuit and equipment protection, or just the required equipment protection. This required protection for fixed outdoor deicing and snow-melting equipment may be accomplished by using circuit breakers equipped with ground-fault equipment protection (GFEP) or an integral device supplied as part of the deicing or snow-melting equipment that is sensitive to leakage currents in the magnitude of 6 milliamperes to 50 milliamperes [referred to by UL as ground-fault equipment protection circuit interrupters (GFEPCI)]. These protection devices, if applied properly, will substantially reduce the risk of a fire being started by low-level electrical arcing.
It is important to understand that this required equipment protection is not the same as a ground-fault circuit interrupter used for personal protection that trips at 5 milliamperes (?1 milliampere).
For further information regarding ground-fault equipment protection used to comply with 426.28 and 427.22, refer to the UL General Information for Electrical Equipment Directory (White Book), category KCZI.
 

celtic

Senior Member
Location
NJ
Celtic, you finished my paragraph lol. I heard about all those color books the other day, man they are expensive, I wont be buying them anytime soon.

Oh come on...it's got pictures! :D

The dwelling unit shown in Exhibit 210.11 has four outdoor receptacles. Three of these receptacles are considered to be at direct grade level access and must have GFCI protection for personnel. The fourth receptacle located adjacent to the gutter for the roof-mounted snow-melting cable is not readily accessible and, therefore, is exempt from the GFCI requirements of 210.8(A)(3). However, this receptacle is covered by the equipment protection requirements of 426.28. See the commentary following 210.52(E) and 406.8(B) regarding the installation of outdoor receptacles subject to moisture.

Exhibit21011.jpg


Exhibit 210.11 A dwelling unit with three receptacles that are required by 210.8(A)(3) to have GFCI protection and one that is exempt because it is not readily accessible.
[NOTE: Above is from the '02 NECH]
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
NECH? I buy one every other code cycle. Won't have to buy the 2011 - if I have that much cash, i can retire:)
 