nvcape

Senior Member
Re: SO cable in IMC conduit

Thanks, I was just about to ask the same thing. NEC 400.8 says USES NOT PERMITTED: "Where installed in raceways, except as otherwise permitted in this CODE" Does anyone know which sections permit this?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: SO cable in IMC conduit

No, SO cord cannot be run in conduit.

Does anyone know which sections permit this?

See 400.7. I might ask why you would want to run SO cord in conduit in the first place? :confused:
 

nvcape

Senior Member
Re: SO cable in IMC conduit

Here, someone wanted to use a length of conduit to lower pendant HID fixtures (beteen the hook and fixture) and wanted to run the SO through the conduit. As far as I am concerned, NEC 410-30 (c) says you can't, even though 400-7 lists pendants.
 