So called Electrician

Status
Not open for further replies.

Jackfl

Member
Location
Florida
I was looking in the codebook at Article 680 for GFCI Protection for a 3 Phase motor to a Fountain.680.51 is it for Submersible pump only?
680.50 see Part II and 680.21(C) is for Single-Phase.
Where will find the answer?
 
I was looking in the codebook at Article 680 for GFCI Protection for a 3 Phase motor to a Fountain.680.51 is it for Submersible pump only?
680.50 see Part II and 680.21(C) is for Single-Phase.
Where will find the answer?

Jack,
Is this a Cord-and-Plug Connected equipment ?
3-phase Cord-and-Plug ?
You said "submersible".

""680.56 Cord-and-Plug-Connected Equipment.""

""(A) Ground-Fault Circuit Interrupter. All electrical
equipment, including power-supply cords, shall be pro-
tected by ground-fault circuit interrupters.""

""(B) Cord Type. Flexible cord immersed in or exposed to
water shall be of a type for extra-hard usage, as designated
in Table 400.4, and shall be a listed type with a “W” suffix.""
 