B brandtew Member Oct 31, 2012 #1 Can someone tell where in the NEC does it not allow outlet boxes at the end of a SO cord to have knockouts
Can someone tell where in the NEC does it not allow outlet boxes at the end of a SO cord to have knockouts
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 31, 2012 #2 314.23(H)(1) is normally cited for that application.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Oct 31, 2012 #3 brandtew said: Can someone tell where in the NEC does it not allow outlet boxes at the end of a SO cord to have knockouts Click to expand... This is not a clear NEC issue. OSHA tends to not like the knockouts (someone's finger could enter a missing one), but the NEC usually gets blamed for it. Along with Don's reference, don't forget the catch-all 110.3.
brandtew said: Can someone tell where in the NEC does it not allow outlet boxes at the end of a SO cord to have knockouts Click to expand... This is not a clear NEC issue. OSHA tends to not like the knockouts (someone's finger could enter a missing one), but the NEC usually gets blamed for it. Along with Don's reference, don't forget the catch-all 110.3.