SO Cord for lighting

Status
Not open for further replies.

sharan

Senior Member
Can SO cord connecting between linear LED fixtures outdoor (façade ltg) be 10'? Is there a maximum limitation in length? This is in Chicago.
 
Type SO flexible cord (not cable!)
Is not allowed for use as part of the building wiring system (and I think that between luminaires qualifies.)
Unless you can meet one of the vibration, motion, or frequent moving of equipment exceptions, that is.
If the LED feed is low voltage, with limited power, you may be able to use landscape wire.