A discussion came up in class tonight.
In Soares 'Book on Grounding'...Chap. 20 - Tables, there is a table entitled "Maximum length of steel conduit or tubing that may safely be used as an equipment grounding circuit conductor"
Bottom line, there's been testing done by the Georgia Institute of Technology and they feel there is a length limit to various sizes and types of conduit that will safely clear a fault.
I know 250.118 lists these conduits as 'Types of EGCs' and makes no mention of length limitations.
However - 250.4(A)(3) & (5) establishes a performance criteria for any bonding system. That is, even if you do install a system correctly, using all the right listed components....installed per mfr's instructions, etc., there is still a performance criteria that must be met. To whit - the system must be able to clear a fault.
With Georgia Tech providing test results indicating there is a performance deficiency when using steel conduit as an equipment grounding conductor in lengths greater than those in the table, would it be fair for an inspector to ask for performance verification for an installed system when those table lengths are exceeded. [I know Georgia Tech is not the code book - but they have performed, I would think, credible testing that shows performance deficiencies].
I'm not talking inches here...those table indicate no conduit 'may safely be used' in lengths greater than 300 ft. I talking about looking at a job with lengths of 500+ feet.
An analogy: Table C.1 - EMT - says I can install 9 #12 THHN conductors in 1/2" EMT conduit; however 300.17 says the number of conductors in any raceway shall not be more than will permit...ready installation or withdrawal of the conductors without damage to the conductors or to their insulation. I know if you try to pull (9) solid #12s in 1/2" EMT with a couple 90s you're going to damage the insulation. So even if you were code compliant with respect to fill, you still have not met the performace criteria of 300.17.
I'm not saying to use the Soares tables to red tag a job, I'm asking would it be legitimate to ask for performance verification?
In Soares 'Book on Grounding'...Chap. 20 - Tables, there is a table entitled "Maximum length of steel conduit or tubing that may safely be used as an equipment grounding circuit conductor"
Bottom line, there's been testing done by the Georgia Institute of Technology and they feel there is a length limit to various sizes and types of conduit that will safely clear a fault.
I know 250.118 lists these conduits as 'Types of EGCs' and makes no mention of length limitations.
However - 250.4(A)(3) & (5) establishes a performance criteria for any bonding system. That is, even if you do install a system correctly, using all the right listed components....installed per mfr's instructions, etc., there is still a performance criteria that must be met. To whit - the system must be able to clear a fault.
With Georgia Tech providing test results indicating there is a performance deficiency when using steel conduit as an equipment grounding conductor in lengths greater than those in the table, would it be fair for an inspector to ask for performance verification for an installed system when those table lengths are exceeded. [I know Georgia Tech is not the code book - but they have performed, I would think, credible testing that shows performance deficiencies].
I'm not talking inches here...those table indicate no conduit 'may safely be used' in lengths greater than 300 ft. I talking about looking at a job with lengths of 500+ feet.
An analogy: Table C.1 - EMT - says I can install 9 #12 THHN conductors in 1/2" EMT conduit; however 300.17 says the number of conductors in any raceway shall not be more than will permit...ready installation or withdrawal of the conductors without damage to the conductors or to their insulation. I know if you try to pull (9) solid #12s in 1/2" EMT with a couple 90s you're going to damage the insulation. So even if you were code compliant with respect to fill, you still have not met the performace criteria of 300.17.
I'm not saying to use the Soares tables to red tag a job, I'm asking would it be legitimate to ask for performance verification?