I have 208V single phase soda disp/ ice maker 6.3kw. The breaker provided is 30A. Would breaker sizing for disp/ice maker be in which section NEC 2017?
I would call it an appliance. Article 422. Take a look at 422.3.I have 208V single phase soda disp/ ice maker 6.3kw. The breaker provided is 30A. Would breaker sizing for disp/ice maker be in which section NEC 2017?
Does this work?
6300/208=30.29 amps, drop the .29=30 amps.
Well then:Oh no! Its three phase
422.11(E) 30 amp breaker permissible.. You are good to go !Well then:
6300/208/1.73=17.5 amps.