R ron g Member Jul 20, 2005 #1 I need to run wire in soffit on a appartment building.What are the rules for this?I only need to go 35 feet for a sensor light.
I need to run wire in soffit on a appartment building.What are the rules for this?I only need to go 35 feet for a sensor light.
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager Jul 20, 2005 #2 Re: soffit run Go for it.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 20, 2005 #3 Re: soffit run You can run a cable through a soffit to feed your sensor light. If the soffit is accessible than the cable will need to be supported and secured. If it is fished through the hollow spaces of the soffit than securing it isn't required.