Hendrix
- New England
Need GFCI protection ???????????
This one is in the restruant dining room.of course most areas we install them are considered "kitchen" so its a requirment.
Not a "vending machine" but a "dispenser".
Nor I. Do it all the time :huh:Yeah, I misread post. Not uncommon for me.:slaphead:
422.51 Cord-and-Plug-Connected Vending Machines.
Cord-and-plug-connected vending machines manufactured
or re-manufactured on or after January 1, 2005, shall include
a ground-fault circuit interrupter as an integral part of
the attachment plug or be located within 300 mm (12 in.) of
the attachment plug. Older vending machines manufactured
or remanufactured prior to January 1, 2005, shall be connected
to a GFCI-protected outlet. For the purpose of this
section, the term vending machine means any self-service
device that dispenses products or merchandise without the
necessity of replenishing the device between each vending
operation and is designed to require insertion of a coin,
paper currency, token, card, key, or receipt of payment by
other means.
Edit, I misread OP.
Unless this unit is in a bathroom, kitchen, on a roof top, or outdoors, GFCI protection is not required.
GFCI protection is not prohibited either though.
I believe you quoted the correct article, and yes, they need to be gfci protected.
I disagree, see 422.51
Vending Machine. Any self-service device that dispenses products or merchandise without the necessity of replenishing the device between each vending operation and is designed to require insertion of coin, paper currency, token, card, key, or receipt of payment by other means.
See 422.2 Definition:
If this soft drink dispenser does not require insertion of coins, currency, credit cards, or other payment methods before it will dispense product, then it is not a vending machine by definition of this article.