I have a customer that is having issues with about 50% of the HPS hid’s going out every time the compressor starts. 30 hp line voltage starter, 208 volt three phase. It’s an obvious voltage drop issue, looking at what options I have. The compressor people say it’s working perfect, but I hear it struggling to start, and I don’t hear the unloader firing after it shuts off. Inrush is 333 amps. POCO is a little high (216 volts) , but drops to 200 on start up at the service, but running is at 208. Looks like they have one or two parallel 4/0 aluminum 150’ to the service, which is 800 amp. The compressor feeder is also a little on the small side, as it is #1 cu @ 130’. Anyway, can softstarts be used on air compressors? I’ve used them on fire pumps and large refrigeration compressors, but not on piston type air compressors.