Johnboy2316
Member
- Location
- Texas
- Occupation
- Industrial electrician
I recently had a service call to a hot mix asphalt plant where they were having trouble with their exhaust fan. Upon arrival I immediately began testing their motors ( 2 200hp motors turning the same pulley connected to a fan). I discovered that one of the 2 motors megged bad so I had it replaced. Their original setup consisted of 2 separate soft starts , one for each motor. It’s been my experience that this type of setup is more prone to problems than a single soft start oversized to 125% of the combined nameplate FLA. I installed a single Toshiba that is good for 500hp or 600A. I am going back later this week to install separate motor overloads for the two motors but for now I just have the drive programmed to protect both motors together. The issue is that from time to time they still go down on “OLC” which means overcurrent at speed. This doesn’t seem right because once the fan starts the combined load stays steady at around 413amps which is far less than the 480amps ( 240amps per motor ) that is the combined fla. on top of that the soft start is programmed at 520amps right now and allows 600% of this for startup. That’s more than enough to get these motors running. I can’t even get them to start at all unless I set the ramp time extremely low ( 5 sec ). If I try to let the motors start slowly , say 30sec , it will go down every time on overcurrent. You can spin the fan pulley by hand with the V-belts removed so at first I didn’t think the issue was mechanical. Now I’m not so sure. It still fails to start sometimes. My current settings are FLA 520 ( because it won’t start at 480 ) , service factor 1.15 , in rush 600% of FLA , ramp time 5 sec. Once it’s running it stays at nice comfortable 413A or so. Does anyone have any ideas? My customer has spent over 30K so far and that doesn’t include lost production. I plan to check the fan itself for buildup and check the fan bearings when I go to install the individual overloads. Please Help.