Soft start wiring

Status
Not open for further replies.

sparkyhotmix

Member
Location
Fenwick
Occupation
Maintenance
I have one soft start and a bypass contactor driving 2 - 125 hp motors each motor has overloads fla are 140 amp what size wire is needed to feed the drive and bypass Contactor also what size breaker I think a 400 amp breaker with 350 mcm is right
 
350 is too small...the minimum ampacity for a feeder conductor supplying two 3 phase, 480 volt, 125 hp motors would be 351 amps.
The code would permit the feeder breaker to be 600 amps.
 