Re: Soil enhancement for ground rods?
I believe bennie was trying to research the 25 ohm, question.
My belief has always been that this number 25, 5 less than one (all seen in spec.s ) is a number that showed up somewhere and like most spec.s was photo copied into the next set of spec.s
I've asked this question of design engineers and the most often response was Company Standard.
But if one wants less than any number why not test before installation so a design can be arrived at that meets spec'.s not reverse engineer the grounding electrode.
I also believe more sweat is loss over this issue that whether the overall grounding system for a particular project is safe and adequate.
Such as testing for neutral to ground connections downstream from the main service or SDS.
In addition this less that ________ (insert number here) value is seldom if ever tested after installation. WE sweat out the first test and never go back for a retest, especially after a lightning strike, drought ect.........
Not trying to say a adequate grounding electrode is not important, just some thoughts.