Soil Thermal Resistivity

Status
Not open for further replies.

timm333

Senior Member
Location
Minneapolis, MN
Occupation
Electrical Design Engineer
I am trying to figure out what are the correct units of soil thermal resistivity. The acceptable soil thermal resistivity is 0.9. In NEC they call it 0.9 C.m/W, but in IEC they call it 0.9 K.m/W. (Where C.m/W = [degree Centigrade.meter/watt], and K.m/W = [degree Kelvin.meter/watt]). I am trying to figure out why the value "0.9" does not change even though the units are change. Thanks for help.
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
I am trying to figure out what are the correct units of soil thermal resistivity. The acceptable soil thermal resistivity is 0.9. In NEC they call it 0.9 C.m/W, but in IEC they call it 0.9 K.m/W. (Where C.m/W = [degree Centigrade.meter/watt], and K.m/W = [degree Kelvin.meter/watt]). I am trying to figure out why the value "0.9" does not change even though the units are change. Thanks for help.


0 C = starts at freezeing point of water, 0 K starts at absolute zero. Units have same dimension, so 0.9 does not change.

Just like F and R unless that is just more confusing?
 

Phil Corso

Senior Member
Timm,

The units are equal because you are dealing with temperature change! That is, deg ⁰C (differential) is equal to K (differential)! Also, the correct units are ⁰C·m/W, and K·m/W! There is no deg ‘⁰’ assigned to K!

Regards, Phil Corso
 