solarken
NABCEP PVIP
- Location
- Hudson, OH, USA
- Occupation
- Solar Design and Installation Professional
I'm designing a system with the Sol-Ark 15K and looking for guidance.
The line diagrams Sol-Ark provides all show a 200A fused disconnect ahead of the inverter. Has anyone used the Grid breaker integrated into the Sol-Ark as a service disconnect? I can't find breaker ratings in the documentation.
The data sheet shows 10AWG max for the PV Inputs. Has anyone found 8AWG will fit?
The specs say it has 690.12 Rapid Shutdown integrated, but it looks like a Sunspec PLC transmitter functionality may not be built-in. Is this the case, and what solutions have you used?
Customer wants to use EG4LL batteries. On EG4 website it says their batteries work with Sol-Ark in closed loop mode, but I don't see EG4 listed on Sol-Ark site as a compatible battery partner. Any insight?
Thanks, Ken
The line diagrams Sol-Ark provides all show a 200A fused disconnect ahead of the inverter. Has anyone used the Grid breaker integrated into the Sol-Ark as a service disconnect? I can't find breaker ratings in the documentation.
The data sheet shows 10AWG max for the PV Inputs. Has anyone found 8AWG will fit?
The specs say it has 690.12 Rapid Shutdown integrated, but it looks like a Sunspec PLC transmitter functionality may not be built-in. Is this the case, and what solutions have you used?
Customer wants to use EG4LL batteries. On EG4 website it says their batteries work with Sol-Ark in closed loop mode, but I don't see EG4 listed on Sol-Ark site as a compatible battery partner. Any insight?
Thanks, Ken