Trenched AC wires run from a detached shed/garage/ground mount with solar to a house.
Normally before I penetrate a house I would place an AC disconnect on the exterior wall of the house.
Following NEC 2017,
"225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure served or
where the conductors pass through the building or structure.
The disconnecting means shall be at a readily accessible location
nearest the point of entrance of the conductors. For the
purposes of this section, the requirements in 230.6 shall be
utilized."
I have this one job where the customer is wanting us to penetrate the basement from the trench, run conduit across basement,
then penetrate back out to exterior wall, and then place a rapid shutdown disconnect next to the utility meter.
Normally I would be installing two disconnects, with one near utility meter and another disconnect prior to the wires from the solar array entering the building.
Looking at this forum most of the posts that I saw concerning this are prior to rapid shutdown and prior to 2017.
In NEC 2017,2020,or 2023, is there anything in the code that only requires the rapid shutdown device where 225.32 does not apply?
Can I get away with the one disconnect by the utility meter?
Normally before I penetrate a house I would place an AC disconnect on the exterior wall of the house.
Following NEC 2017,
"225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure served or
where the conductors pass through the building or structure.
The disconnecting means shall be at a readily accessible location
nearest the point of entrance of the conductors. For the
purposes of this section, the requirements in 230.6 shall be
utilized."
I have this one job where the customer is wanting us to penetrate the basement from the trench, run conduit across basement,
then penetrate back out to exterior wall, and then place a rapid shutdown disconnect next to the utility meter.
Normally I would be installing two disconnects, with one near utility meter and another disconnect prior to the wires from the solar array entering the building.
Looking at this forum most of the posts that I saw concerning this are prior to rapid shutdown and prior to 2017.
In NEC 2017,2020,or 2023, is there anything in the code that only requires the rapid shutdown device where 225.32 does not apply?
Can I get away with the one disconnect by the utility meter?