shortcircuit2
Senior Member
- Location
- South of Bawstin
Do all components need to be LISTED by a NRTL for use together to be used for grounding? Specifically, I?m referring to the PV modules with a mounting or ?racking system?...
Example:
1. The PV rail mounting system needs to be LISTED as suitable for grounding and not just mounting.
2. The PV module needs to be LISTED for all the different methods for grounding. IE: Grounding with nut, bolt and lug, or grounding with self tapping screw and lug, or grounding by WEEB system, or any other grounding method.
In reading the installation instructions of 2 different PV module manufacturers recently, 1 only describes the use of a nut & bolt with grounding lug to the panel for grounding, and the other describes 5 different ways to ground the module.
So, the PV module with only 1 method for grounding can only be grounded that way or the 1703 listing is void.
This 45-minute UL webinar seems to discuss this in detail...(Its long, but informative)
http://content.learnshare.com/courses/73/424588/UL 2703/lib/playback.html
After watching this, my conclusion is that all components do need to be tested and NRTL LISTED together.
Would this need to be done at both 600volts and 1000volts?
shortcircuit
Example:
1. The PV rail mounting system needs to be LISTED as suitable for grounding and not just mounting.
2. The PV module needs to be LISTED for all the different methods for grounding. IE: Grounding with nut, bolt and lug, or grounding with self tapping screw and lug, or grounding by WEEB system, or any other grounding method.
In reading the installation instructions of 2 different PV module manufacturers recently, 1 only describes the use of a nut & bolt with grounding lug to the panel for grounding, and the other describes 5 different ways to ground the module.
So, the PV module with only 1 method for grounding can only be grounded that way or the 1703 listing is void.
This 45-minute UL webinar seems to discuss this in detail...(Its long, but informative)
http://content.learnshare.com/courses/73/424588/UL 2703/lib/playback.html
After watching this, my conclusion is that all components do need to be tested and NRTL LISTED together.
Would this need to be done at both 600volts and 1000volts?
shortcircuit