N nosparks1 Member Oct 1, 2010 #1 2008 NEC Article 690.47 (D), Is the article stating that "Additional" electrodes are required or stating the requirements "IF" they are installed.
tallgirl Senior Member Location Glendale, WI Occupation Controls Systems firmware engineer Oct 1, 2010 #2 nosparks1 said: 2008 NEC Article 690.47 (D), Is the article stating that "Additional" electrodes are required or stating the requirements "IF" they are installed. Click to expand... It's a "SHALL", so you have to do it. The confusion is that a pole or ground mount array may already have enough metal that is in contact with dirt to count as a grounding electrode, in which case the second paragraph applies.
acrwc10 Master Code Professional Location CA Occupation Building inspector Oct 2, 2010 #3 Exception 1. is interesting. I'm not sure I know what this would apply to. Exception No. 1: Array grounding electrode(s) shall not be required where the load served by the array is integral with the array.