How would one categorize (not sure if thats the right term) the output of the current transformers used in Solar? The only thing I can find in enphase documentation is that theyre not class 2 and do not use class 2 wiring methods.
These are not the typical 0-5A CTs that are used for instrumentation and such. The ones from Enphase have a sticker that says 200A 0.5v. The instructions say if the leads are extended they should be twisted. The contractor in question has been using twisted 18ga 600v UL1015 MTW, same as the factory wires on the CTs. There has been a couple times where an inspector has rejected use of that wire, but allowed THWN to replace it. I believe this is because of it not having a NEC wire type printed on it besides MTW. I believe I have a solution with TFFN which is specifically listed as one of the acceptable wire types in 18ga for class 1, but I need to make sure I've got this right.
These are not the typical 0-5A CTs that are used for instrumentation and such. The ones from Enphase have a sticker that says 200A 0.5v. The instructions say if the leads are extended they should be twisted. The contractor in question has been using twisted 18ga 600v UL1015 MTW, same as the factory wires on the CTs. There has been a couple times where an inspector has rejected use of that wire, but allowed THWN to replace it. I believe this is because of it not having a NEC wire type printed on it besides MTW. I believe I have a solution with TFFN which is specifically listed as one of the acceptable wire types in 18ga for class 1, but I need to make sure I've got this right.