Solar disconnect line load
dm9289
Industrial Maintenance Electrician
Pennsylvania
Industrial process repair/ maintenance Electrician
I seen solar at a house today and had a question about the disconnect let me give you some details below
EMT coming off of roof from panels
Connects into combiner
AC output from combiner goes to line side of fused disconnect (lugs shielded plastic)
Wire coming from Utility power panel (hot tapped on line side before main) is on load side of outdoor solar disconnect. Lugs not shielded on load side so always hot even if you shut off disconnect or main panel.
Is this done commonly?
This was a major Solar company?
Or is there a special disconnect that should be used for this purpose?
Thanks in advance
The disconnect was installed backwards, the utility side should be the line side, as you concluded. That's the only way to make it safe to change fuses when the disconnect is open. The grid-tie inverter will automatically deenergize its output when it loses the grid reference.
Cheers, Wayne