Designer101
Senior Member
- Location
- California
- Occupation
- Solar and ESS Designer
we have two SolarEdge(7.6 kw) energy hub inverters and three LG chem batteries.
inverters are connected to 200A Back up interface , two back up interface is available one with 200A breaker for creating as service entrance and other without 200A breaker into it. here i have used without the 200A breaker.
we have tried to back up the 225 A sub panel, that sub panel is initially connected to 200A split type 400A Rated main panel.
Since the sub panel and main panel are located greater than 60 ft. apart and at opposite site of building, relocation the Sub panel load to main panel is not so easy and the sub panel breaker cannot be derated to 150 A, we need at least 80A of back feed.
Now how to make this code compliant installation.
A part of me tells me that since we are connecting the back up interface directly to main breaker we don't have to follow 120 percent rule and we can use 705.12 (c), to qualify. I want to take a suggestion before submitting for permitting.
please see attached SLD.
inverters are connected to 200A Back up interface , two back up interface is available one with 200A breaker for creating as service entrance and other without 200A breaker into it. here i have used without the 200A breaker.
we have tried to back up the 225 A sub panel, that sub panel is initially connected to 200A split type 400A Rated main panel.
Since the sub panel and main panel are located greater than 60 ft. apart and at opposite site of building, relocation the Sub panel load to main panel is not so easy and the sub panel breaker cannot be derated to 150 A, we need at least 80A of back feed.
Now how to make this code compliant installation.
A part of me tells me that since we are connecting the back up interface directly to main breaker we don't have to follow 120 percent rule and we can use 705.12 (c), to qualify. I want to take a suggestion before submitting for permitting.
please see attached SLD.