We have seen a significant increase in applications for roof mounted solar systems and have been diligently working on improving our review process. One item I keep seeing, and have spent a lot of time researching, is the sizing of the equipment grounding conductor. It is very common for the contractor to use a 6AWG EGC on the roof and then after the junction box or invertor they reduce the size to an 8 or 10. The 6 is oversized for what is required but I believe they use it because it is the minimum size that does not require protection so they can run it without conduit. My concern is that by reducing the size along the path to the grounding electrode, you are possibly creating a "choke" point or an impedance. The NEC identifies when or how you can increase the size of an EGC but I cannot find anything allowing the size to be reduced.