JP23
Member
- Location
- California
The scenario is a 277/480 3 ph. 4w. utility side bus tap to a 1200 amp disconnect for a solar installation. The available space
in the switch gear for the taps does not appear large enough for all of the parallel conductors
required. There is a single 10 ft. 3r gutter spanning over each termination point with myers hubs and nipples.
The project engineer is saying that any welding wire will suffice and 4/0 will carry 400 amps.
I have never seen this in any permanent building wiring scenario and am questioning it. I did find
a post where someone said if the welding wire had the RHH/RHW rating it
would be acceptable to use. Any advice on this would be appreciated.
in the switch gear for the taps does not appear large enough for all of the parallel conductors
required. There is a single 10 ft. 3r gutter spanning over each termination point with myers hubs and nipples.
The project engineer is saying that any welding wire will suffice and 4/0 will carry 400 amps.
I have never seen this in any permanent building wiring scenario and am questioning it. I did find
a post where someone said if the welding wire had the RHH/RHW rating it
would be acceptable to use. Any advice on this would be appreciated.