rayp1
Member
- Location
- Phoenix, Az, USA
Situation: 25 dry type 480-3W/480V-4W transformers each serve one remote Panel. The secondary conductors are longer than 100 feet. One option to be code compliant versus a coordination study under consideration is to install this same room as the transformer multiple SWBD's containing the protection for the secondary conductors feeding the remote load circuit Panels.
Also, the cable tray system is rated and labeled as an equipment grounding conductor.
Question: Do you see any code violations or concerns with the attached diagram.
Also, the cable tray system is rated and labeled as an equipment grounding conductor.
Question: Do you see any code violations or concerns with the attached diagram.