CNYSolar
New member
- Location
- Canastota NY USA
I have a unique situation which I'll try to explain..
Two parallel sets of 500mcm's feed an 800A switch gear from the utility. We have a 400A panel board with no loads (potentially 240A max of backfed PV). Going to the 800A parallel fed switch gear with one set of 500mcm. I understand 310.10(H)(2) and maintaining length/characteristics of conductors. Other than this what would be the reason you could not tap the 400A panel onto one set of feed conductors near the bus bar. As opposed to rebuilding the inside of the 800A gear to accommodate the new 500mcm tap conductors. Is the problem here the potential to increase the load on the conductors and operating temperature? Because if it is only capable of back feeding wouldn't it only decrease the load on one set of parallel conductors?
Also if you tap both parallel sets of conductors at the same point to the new 400A PV only panel (which has a main breaker of 300A) does this alleviate the problem without creating additional risks?
Two parallel sets of 500mcm's feed an 800A switch gear from the utility. We have a 400A panel board with no loads (potentially 240A max of backfed PV). Going to the 800A parallel fed switch gear with one set of 500mcm. I understand 310.10(H)(2) and maintaining length/characteristics of conductors. Other than this what would be the reason you could not tap the 400A panel onto one set of feed conductors near the bus bar. As opposed to rebuilding the inside of the 800A gear to accommodate the new 500mcm tap conductors. Is the problem here the potential to increase the load on the conductors and operating temperature? Because if it is only capable of back feeding wouldn't it only decrease the load on one set of parallel conductors?
Also if you tap both parallel sets of conductors at the same point to the new 400A PV only panel (which has a main breaker of 300A) does this alleviate the problem without creating additional risks?