I have a PV system with the lines terminating on the north end of a residence and the existing service drop is on the south end. In this jurisdiction POCO requires that the PV system feed to the service lines and not to the service panel.
Previous installations have been made by adding a second riser for the PV system at the original service location and POCO jumps them at the drop.
The installer wants to add a service drop for the PV at the north end citing 690.56 as justification.
My position is that 690.56 allows for a remote disconnect but does not allow for a second set of service drop conductors.
What say you ?
Previous installations have been made by adding a second riser for the PV system at the original service location and POCO jumps them at the drop.
The installer wants to add a service drop for the PV at the north end citing 690.56 as justification.
My position is that 690.56 allows for a remote disconnect but does not allow for a second set of service drop conductors.
What say you ?