Solar PV Micro Inverter Interconnection

Status
Not open for further replies.

happysanghvi

New member
Location
Lowell, MA
We are doing one solar PV project where, we would like to have 68 enphase inverters.


The client has 240V, 3 Phase service. We would like to use M250 micro inverters, which is rated at 208V, 3 phase. How can we use these inverters if we want to use this for our project? Also, I would like to know how would we recombine more than 3 strings ?


Please write me back whenever you get a chance.

Thank You!:D
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
With these inverters your options are limited...

Option 1: use a transformer to create a 208/120 wye to connect the solar to.

Option 2: IF it is a high-leg delta, connect 240V to the A-C phase and neutral. Do not use the high-leg.

You had best ask the utility which is the better option. If it's a high-leg delta and the high-leg is not rated for a high current then you are probably better off with option 2. See the recent thread on connecting to an open delta. If the service is designed for a relatively balanced 3-phase load, the transformer option might be what you have to do.
 