Scenario: We are feeding the AC output from 3 x SolarEdge 33 kW 3-phase inverters into a dedicated AC Combiner Panel. Each Inverter outputs 40 Amps and will directly connect to a 3-Pole 50 Amp breaker upsized by 1.25 for Continuous load. That gives a total Amperage of the sum of these breakers of 150 Amps. It is a dedicated AC solar panel and the output of the panel are a set of 4/0's running down the building to a Main Disconnect and Main Panel.
Question: Given the sum of the breakers being 150 Amps. According to NEC code 705 .12(D)(2), the 120% rule, couldn't the main breaker could also be 150 Amps? So what would the minimum Busbar rating need to be?