Hello everyone this is my first post. I'm having a problem with the single line drawing. My first drawing was rejected by DTE. This is my new drawing. These are the comments I got back from the engineer assigned to review the drawings. Based on did Engineers comment What have I done wrong here? Thank you for being gentle the first time.
Best explained with pictures drawings and words.
Engineers comment
Thank you for sending the new One-line. The presentation of the CT cabinet looks correct now. You only need to include, as mentioned in the previous email, the AC disconnect (blade style) between the Generation meter (PV Meter) and the CT cabinet.
Once we have all the info, we will open the application and submit it to speed up the process.
section_05.pdf
Please revise the SIM book section 5-4-14 for more information on those rules. (Page 76).
Single line dwg
Best explained with pictures drawings and words.
Engineers comment
Thank you for sending the new One-line. The presentation of the CT cabinet looks correct now. You only need to include, as mentioned in the previous email, the AC disconnect (blade style) between the Generation meter (PV Meter) and the CT cabinet.
Once we have all the info, we will open the application and submit it to speed up the process.
section_05.pdf
Please revise the SIM book section 5-4-14 for more information on those rules. (Page 76).
Single line dwg