Buchanan makes a UL listed tap (BTap) that says “suitable for use on line side of the service equipment”. Just failed an inspection for using an ilsco and the Burndys (which are identical to the BTap but serial numbers are different) aren’t suitable but UL listed. This has been an issue since the first of the year everywhere but this is the only device I found that is suitable for line side of service equipment and allowed me to pass my inspection. Buchanan BTap Cat # BTC4/0-10 is what I used (service conductors 4/0-3 AWG and tap 2-10 AWG) and has a tap amp rating of up to 130 amps (which you’ll never get to off res solar), misinterpreted thinking it was the service amperage.