My friend's house has grid tied solar. Now here's the kicker:
It ties directly to the exterior main service panel which only has a single 100A breaker.
The 100A breaker feeds both an interior service panel via some very large wires (I think they are #1 ga), and the solar's breaker box via #12ga wires, but with no breaker (other than the 100A breaker) between the 100A breaker and the solar breaker.
The #12 wires are tapped into the #1 wires just downstream of the 100A breaker with something that looks like a cable clamp.
In other words the #12 wires are protected only with the 100A breaker!
AC MAINS ==>
100A Breaker ==>
#1ga wires ==> Interior service panel
& #12ga wires---> Solar 20A breaker
It is my understanding that all wires must be protected upstream by a breaker of appropriate size to protect them.
In this case the #12 wires have only a 100A breaker upstream.
This doesn't seem sensible, nor reasonable, nor legal to me. But what do I know? Perhaps there is some code exception that I'm not aware of, but I don't think so.
It ties directly to the exterior main service panel which only has a single 100A breaker.
The 100A breaker feeds both an interior service panel via some very large wires (I think they are #1 ga), and the solar's breaker box via #12ga wires, but with no breaker (other than the 100A breaker) between the 100A breaker and the solar breaker.
The #12 wires are tapped into the #1 wires just downstream of the 100A breaker with something that looks like a cable clamp.
In other words the #12 wires are protected only with the 100A breaker!
AC MAINS ==>
100A Breaker ==>
#1ga wires ==> Interior service panel
& #12ga wires---> Solar 20A breaker
It is my understanding that all wires must be protected upstream by a breaker of appropriate size to protect them.
In this case the #12 wires have only a 100A breaker upstream.
This doesn't seem sensible, nor reasonable, nor legal to me. But what do I know? Perhaps there is some code exception that I'm not aware of, but I don't think so.