The newest approved 2008 nec code book states that all 110 volt and 230 volt swimming pool pumps must be GFI protected, what do I do about 90 volts DC?
Good question however, the code requires only 125V or 240V pumps to have gfci protection. I would say the 90V DC does not req. gfci.
That being said I might feel uncomfortable with that install.
LarryFine
Henrico County, VA
Doc, welcome to the forum! :)
Where is the AC converted to DC? Maybe the AC supply should still be GFCI'ed.
BillK-AZ
Mesa Arizona
DC ground fault?
DC ground fault?
There is no listed equipment for this, but there are components that are used in PV systems for a related ground fault detection.
Xantrex (now a division of Schneider, once known as Trace) used to sell a ground fault detector for solar electric systems that consisted of a custom assembly of one 1-amp and 1 to 4? higher current circuit breakers with a common trip. The DC side of the inverter/charge controller/batteries/array was isolated from ground except for a connection through the 1-amp breaker. If a ground fault developed anywhere in the system, the 1-amp breaker would provide the return path for the fault current and trip if it exceeded 1-amp. This would trip the larger breakers and shut down the system. This is not sensitive enough to protect people from the shock hazard, only intended to prevent other safety problems.