Devendra Rajwade
- CA
- engineer
I would like to get some help with an issue with one of the solar systems.
This is on a farm with 300HP pump-motor connected to a VFD. 3ph - 480/277V Power from the utility transformer terminates line side at 400AMp breaker in VFD cabinet going through the utility meter cabinet. Breaker has three termination lugs on each side. Wires from two load side lugs are connected to the VFD and the the 3rd load side lug is used to terminate the solar system. Solar side consists of two 66.6kW Solaredge 3Ph-480/277V inverters, whose combined output (160A) is connected to the breaker through a fused disconnect
Here is the problem, Inverters run normally when pump is off. If inverters are producing power and then the pump is turned on they continue to run normally. If pump is running and then you start the inverters they will not produce power and go into starting loop. This scenario is usually in the morning when pump is running over night and inverters wake up in the morning as the sun rises.
Solaredge support is aware of the issue but has not provided any resolution. Any guidance in identifying the cause is appreciated.