jc95
- California
- retired electrical engineer
I have a SE 7600H with SE Backup Interface & SE battery. We had a recent grid outage. When the outage occurred, the BI switched to inverter and PV sustained the load, then battery after sunset. The battery lasted until the middle of the night when it was depleted and the load lost power. All as expected. At sunrise, however, when the PV could have been producing, the system remained cold & dark. No charging of the battery or powering the load. Nothing until the grid came back up in the afternoon, when the system started working normally again, powering the load, charging the battery, and exporting to the grid.
I expected the system to cold start and at least charge the battery and eventually produce AC to power the load. But it didn't. I have three possible explanations:
1. it is working as intended. No cold-start capability. Grid must be present to start.
2. Installation or configuration error.
3. Faulty firmware or component failure.
SE has an application note regarding generators. I don't have a generator, but in the app note, the generator is behind its own transfer switch and not integrated with the BI or inverter. And the app note is careful to point out that the generator is never connected to the BI. It says when the PV starts producing it will charge the battery while the gen powers the load. Then, the generator is switched off and the BI is connected to the load. No grid power thru all this. That seems to say that #1 is not correct, but it introduces a new possibility:
4. The app note is wrong.