SolarEdge PV Label
Zyb
Maine
Design Engineer
Commercial Project
Module: (237) Silfab 490 HN (490W)
Optimizer: SE P1101
Inverter: (2) SE50KUS
Can anyone verify my label values. Thank you
DC
Operating Current: 314A = (237 x 490) / 370 = (no. of mod x mod power) / min. operating voltage range ??
Operating Voltage: 208V
Maximum System Voltage: 600V
Short Circuit Current: ??
AC
Rated AC Current: 279A = 2 x 139.5
Nom. AC Voltage: 208V
Your DC numbers are all wrong because of the P1101 DC to DC converters. Your DC short circuit current is 18A and the maximum output voltage is 80V times the number of P1101s you have in your longest string unless it is more than the maximum DC voltage that the inverter can take, which in the case of the SE50KUS is 600V.
Thank you
SolarEdge has a whitepaper on labeling your SolarEdge system, that describes the equivalents of labeling a standard PV system adapt to their equipment.