Solenoids in Class I, Div 2 Locations (Sanity Check)

Status
Not open for further replies.

DM2-Inc

Senior Member
Location
Houston, Texas
From what I can tell, 501.105(B)(4) doesn't require a solenoid to be rated for hazardous locations because it does "...not incorporate sliding or make-or-break contacts..."

I'm not sure if the class of coil is a limiting factor, or if there's something elsewhere that would have an affect on this. I'm familiar with the "T" rating relative to installation location but that's not what I'm concerned with.
 
Your understanding 501.105(B)(4) is correct and beyond the T-code there's nothing else to consider.
 