Julius Right
Senior Member
- Occupation
- Electrical Engineer Power Station Physical Design Retired
Cable Ampacity in solid-bottom [metallic] open-top ?usually in a power station-one could calculate it following J.Stolpe-"Ampacities for Cables in randomly filled trays"/1971way.
But in N.E.C. world it is only a tiny mention in-N.E.C. 2011-392.17(2)(c )
"Exception to (2)(3): For solid bottom cable trays the ampacity
of single conductor cables shall be determined by
310.15(C)."
310.15(C) Engineering Supervision. Under engineering supervision,
conductor ampacities shall be permitted to be calculated
by means of the following general equation:
I=sqrt((Tc-Ta)/(Rdc*(1+Yc)*Rca))*10^3 A
How to calculate Rca?:rant:
Nor Neher&McGrath neither IEC 60287 has a reference.
On the other hand, even Stolpe does not give how to calculate Rca since his method it is a global calculation.
But in N.E.C. world it is only a tiny mention in-N.E.C. 2011-392.17(2)(c )
"Exception to (2)(3): For solid bottom cable trays the ampacity
of single conductor cables shall be determined by
310.15(C)."
310.15(C) Engineering Supervision. Under engineering supervision,
conductor ampacities shall be permitted to be calculated
by means of the following general equation:
I=sqrt((Tc-Ta)/(Rdc*(1+Yc)*Rca))*10^3 A
How to calculate Rca?:rant:
Nor Neher&McGrath neither IEC 60287 has a reference.
On the other hand, even Stolpe does not give how to calculate Rca since his method it is a global calculation.