solid vs stranded thhn

Status
Not open for further replies.
Is there any preference between using stranded vs solid thhn below #6 in a boiler house environment where there is no movement, that is, fixed situation. Where we are, solid is cheaper and is no problem at terminations.
 
Is there any preference between using stranded vs solid thhn below #6 in a boiler house environment where there is no movement, that is, fixed situation. Where we are, solid is cheaper and is no problem at terminations.

Yes, it's exactly that, a preference. Stranded pulls easier - potentially a lot easier if it's a full pipe with lots of bends. Solid is easier to terminate on devices without clamps, and it stays neater in panels. Generally I pull stranded.
 
Not too many prefer solid larger than 10 AWG, some don't even like 10 AWG solid.

Only time I recall seeing larger than 10 AWG solid is either bare conductor or really old installations.
 
Yes, it's exactly that, a preference. Stranded pulls easier - potentially a lot easier if it's a full pipe with lots of bends. Solid is easier to terminate on devices without clamps, and it stays neater in panels. Generally I pull stranded.

Change the last word to "solid" instead of "stranded" and this is pretty much what I was going to say, adding that solid is 10 - 15% cheaper.

Caveat, this is for #12 and #14 wire. I buy stranded for #10, though I've pulled my share of solid #10 when it's what I had available.
 
Change the last word to "solid" instead of "stranded" and this is pretty much what I was going to say, adding that solid is 10 - 15% cheaper.

Caveat, this is for #12 and #14 wire. I buy stranded for #10, though I've pulled my share of solid #10 when it's what I had available.
Working alone most of the time, I have found I can pull 14 and 12 stranded by myself in many situations where if it were solid I would need helper. Therefore I almost always use stranded.
 
Is there any preference between using stranded vs solid thhn below #6 in a boiler house environment where there is no movement, that is, fixed situation. Where we are, solid is cheaper and is no problem at terminations.

I do prolly 95% 10/12/14 solid.....

But I will say that the few times I get to handle stranded, it sure feels nice.:happyyes:
 
Change the last word to "solid" instead of "stranded" and this is pretty much what I was going to say, adding that solid is 10 - 15% cheaper.

Caveat, this is for #12 and #14 wire. I buy stranded for #10, though I've pulled my share of solid #10 when it's what I had available.
Out of interest, what proportion of the job cost is wire?
 
We do a lot of adds, changes and moves. Solid wire is very difficult to work with after a few years.
Only have stranded on the shelf.
I carry non insulated crimp connectors for terminations where its not a clamp connection.
 
Not too many prefer solid larger than 10 AWG, some don't even like 10 AWG solid.

Only time I recall seeing larger than 10 AWG solid is either bare conductor or really old installations.

I worked in an old building that use to be the POCO line and office. I found #8 solid in conduit. It was a bear to pull out!
 
Out of interest, what proportion of the job cost is wire?

Good question. I do too many different sized jobs to try to keep track.

I'm rarely pulling difficult runs, but I'm ALWAYS terminating on screws; so solid works better there.

Because of that, on the few times the stranded makes a significant difference on pulling, I usually only have solid on the truck and not wanting to buy more wire. So I just get 'er done.
 
All I have is stranded on my truck, and, if you want some real excitement just let a solid end up in your wire pull with the other stranded conductors by accident.

It'll make you reconsider your professional choices.

JAP>
 
Both. :p

I like to mix solid and stranded, because having a few solid conductors makes it easier to push the wires through the raceway.
 
I like stranded myself. I work exclusively industrial. We occasionally contract out larger jobs and some of these like to use solid. I don't
like running solid into motor peckerheads, or using as feeders to control panels. I don't trust solid to stranded wirenut connections is one
reason. Is this a legitimate concern?

In any case I always ask them to run stranded, and some of them will still run solid. They generally don't get much work after that. I figure
we are paying for the work and it should be done the way we want it provided it's code. I am interested in your opinions as far as using solid
for motor connections. I do realize that motors are wound with solid but the working ends are usually stranded.
 
I like stranded myself. I work exclusively industrial. We occasionally contract out larger jobs and some of these like to use solid. I don't
like running solid into motor peckerheads, or using as feeders to control panels. I don't trust solid to stranded wirenut connections is one
reason.
Is this a legitimate concern?

In any case I always ask them to run stranded, and some of them will still run solid. They generally don't get much work after that. I figure
we are paying for the work and it should be done the way we want it provided it's code. I am interested in your opinions as far as using solid
for motor connections. I do realize that motors are wound with solid but the working ends are usually stranded.

I dont like or trust solid to stranded connections either with wirenuts.
 
Lead the stranded by a hair or two and works fine.

Yep. Says so right in the directions.

Wirenuts are like earplugs. They don't have many steps in the directions, but if you know them, they do work better.

I do find that solid tends to tighten up in a wirenut more quickly, at least it seems like it. Less recoil in the winding, too.
 