Solve this equation!
MD Automation
Maryland
Engineer
The answer is 42.
Ha ha - assuming that's a Hitchiker's Guide joke - then yes that's correct. And Don't Panic.
Aluminum wire + homeowner replacing devices =
Another answer might be...
Aluminum wire + homeowner replacing devices = 2 (sad faced receptacles)
At the risk of anthropomorphizing a duplex outlet - the top one looks like it is shedding a tiny tear for his brother below. The brother on the bottom looks like Ralph from "A Christmas Story", who has naturally shot his eye out with a Red Ryder BB Gun. Just like his Mom knew he would.
Looks like a backsplash on the bottom? Maybe a kitchen counter with a toaster or coffee maker pulling a good sized load across that jumper on the "hot" side (that's a bad joke). Like an awful smelling slow cooker. Not what I want for dinner!
robertd
Maryland
electrical contractor
And the important part, is the receptacle not Al rated? I think the Al rating is being dropped from some receptacles and switches.
gadfly56
New Jersey
Professional Engineer, Fire & Life Safety
First, the upper black insulated conductor appears to be copper, not aluminum. Is there copper-plated aluminum out there? Second, did they snip the tab between the receptacles and put them on different circuits? I can't tell from this picture. Or is this just the easy way to daisy chain multiple receptacles?
kwired
Electron manager
NE Nebraska
EC
Unless specifically designed and marked so, they never were intended for direct connection to aluminum.
Bluegrass Boy
Texas
Commercial/ Industrial/ Maintenance Electrician
Yes.
This was in the kitchen, and there was a whole herd of appliances on the counter. Microwave, coffee maker, toaster,.....
I have seen similar before, but not burned as bad as this one. Too much load on the receptacle.
I have always made joints and pig tailed to the receptacle because of this, so it is not daisy chained.
I have seen several GFCI”s in kitchens that were overheating and melting from downstream loads.
EC - retired
I am inclined to think improper torque had more to do with it than the downstream loads.