Question: Why not use current limiting fuses at the installation to lower available fault current to a panel? This is more of an NEC question than a UL question.
If the fused disconnect is not part of the control panel in question, why couldn't one just use the manufacturers data on the current limitiing fuses and consider the fused disconnect a new power source for the control panel. This way the available fault current to the control panel is determined by what is truly available from the load side of the fuses rather than that useless SB2.2 table. My whole angle on this is that adding the fuses outside means that it is not part of the control panel and maybe is not strictly bound by the infamous UL508, so then the manufacturers data for say J fuses could be used, easily obtaining an available fault current to the panel <10ka. Any thoughts on this?
If the fused disconnect is not part of the control panel in question, why couldn't one just use the manufacturers data on the current limitiing fuses and consider the fused disconnect a new power source for the control panel. This way the available fault current to the control panel is determined by what is truly available from the load side of the fuses rather than that useless SB2.2 table. My whole angle on this is that adding the fuses outside means that it is not part of the control panel and maybe is not strictly bound by the infamous UL508, so then the manufacturers data for say J fuses could be used, easily obtaining an available fault current to the panel <10ka. Any thoughts on this?