Can some one explain why type SOOW stops at #2 AWG in the NEC 400.5 (A)(1) Thanks
M MrJLH Senior Member Location CO Apr 20, 2018 #1 Can some one explain why type SOOW stops at #2 AWG in the NEC 400.5 (A)(1) Thanks
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 20, 2018 #2 Might have something to do with the listing but I see Southwire does not manufacturer it larger than #2. Type G is available thru 500 kcmil.m (3c=85# per ft) Last edited: Apr 20, 2018
Might have something to do with the listing but I see Southwire does not manufacturer it larger than #2. Type G is available thru 500 kcmil.m (3c=85# per ft)
C Cow Senior Member Location Eastern Oregon Occupation Electrician Apr 20, 2018 #3 It's probably because most use Type W or some other variation for sizes larger than that. I know we do. Especially because Type W has a higher ampacity for any given size over SOOW.
It's probably because most use Type W or some other variation for sizes larger than that. I know we do. Especially because Type W has a higher ampacity for any given size over SOOW.