Legrand
Member
- Location
- New Mexico
Ok, I know this has been hammered and hammered on here but I have to set my mind at ease knowing that this will not be inspected, and unfortunately I don't agree with my bosses opinion on it. I've run 4 #6 from MP to 3R sub for hot tub outside, 30A 2p gfi & 20A 1p gfi brkrs to feed hot tub, with 2 #10H and 1 #10egc and 2 #12 H&N (no neutral for motor). Anyway then my employer wants a ground rod driven for the sub panel, and that's it. This hot tub is outdoors sitting directly on the grass.
#1) Don't I need to make and equipotential bonding grid, and tie it in with the motor egc. I don't quite understand where to tie it in, code says; shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes(680.26 (B)) The hot tub has everything factory bonded.
#2) I assume there is nothing wrong with the ground rod even though not required.
#3) Anything I missed? I do have a service receptacle. I'm on 2008 code.
Thank you guys.
#1) Don't I need to make and equipotential bonding grid, and tie it in with the motor egc. I don't quite understand where to tie it in, code says; shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes(680.26 (B)) The hot tub has everything factory bonded.
#2) I assume there is nothing wrong with the ground rod even though not required.
#3) Anything I missed? I do have a service receptacle. I'm on 2008 code.
Thank you guys.