I received noise attenuation information pertaining to an outdoor generator enclosure which indicated a 30dB reduction at 3 feet. I thought it was typical to give these values at 23 feet and asked about this. Here is the response I got:
We can change that to 23 feet if you want.
It really does not matter.
If the unit is 100 db/a at 3 feet (no housing) that means it is est @ 91 db/a at 23 feet.
So 30 db/a reduction at 3 feet = 70 db/a
So 30 db/a reduction at 23 feet = 61 db/a
I'm wondering if given the non-linear nature in which noise drops off with distance, I'm wondering if this is true?