I too have done sound for many clubs and shows and it can be either electrical or audio and even can be the power cords they used to hooked up the equipment.
Let me explain what I'm trying to say.
If a neutral has grounded in one of the receptacle box's or somewhere on its way back to the panel there will be current on the grounding of this circuit, if someone has mis-wired a cord plug by switching the ground and neutral there will be current on the grounding,
Now when we connect two or more pieces of equipment to two different power sources, then connect audio links between them we now have placed a piece of the audio shielding in this path as a parallel conductor and since current takes all paths to source this current will also be on the shielding.
This will impose a 60 hz signal to the amp input and since it is within the frequency range of amplifying it will do just that amplify it.
If this problem is present and the equipment is fed from two different circuits in different conduits it is most likely there is current on the grounding or there is a sub-panel that has the grounds and neutrals bonded or only 3-wires have been run to it.
To find it shut off breakers that don't feed the sound equipment, then turn on each one to find which circuit is causing the ground loop.
If the hum is still there then the circuit feeding the amps or mixer board is subject.
If the load of the amplifiers are the cause then temporally feed the amps from another circuit if it goes away then checkout the circuit that feeds the amps, if it doesn't then check out the mixer board's circuit or any equipment that connected to the mixer board. (Or have the sound men isolate it down to which equipment causes the hum by disconnecting all inputs to the mixer. If still there it has to be either mixer circuit or amps circuit))
Check this circuit out to look for grounded neutrals or just shut off all the circuits in this conduit and remove the neutral(s) from the neutral bar then check to see if there is voltage first then check for continuity to neutral bar. If you have continuity then you have a grounded neutral.
There should never be any current on the grounding after the main disconnect in a building (I'm not talking about the GEC)
Equipment grounds should not have current on them and this includes the conduit. If it does then you have potential for a shock hazard or a fire.
This has been a problem in the sound industry for years and in almost all cases it is because of a neutral grounded or a load pulling power through the grounding, and the fact that many sound men don't know how to wire a plug on the end of a cord.
The only time I ran into a venue that this wasn't the problem was when we had equipment being fed by two different services that did use the grounded conductor as a grounding at each service as allowed in the NEC 230. There was no work around but to install the isolation transformers to keep the bands from using ground cheaters on their equipment power cords.
We had to correct the problem with 1 to 1 isolation audio transformers in the audio feeds to the amp's or the stage DI breakout box I always keep a supply of Switch Craft 1 to 1's handy and in all for mats IE XLR, ?" phono jack, and RCA. with both male and female to accommodate all hookups.
I hope this gives you some insite to the problem.
Many older churchs will have sub panels that are not wired to the NEC by having only 3 conductors to them or haveing the grounding and neutrals on the same buss-bar. Both a no-no but very common.