A few questions:
1) Suppose an engineer tells me that at a certain point in the electrical system, the calculated Available Fault Current on a 240V 2-wire circuit is 12 kA, and that calculation is accurate. Does that mean that it makes sense to say the source impedance is 240V / 12kA = 20 milliohms?
2) By which I mean that if you take, say, a 100A load and connect it at that point, the upstream voltage drop will be 100A * 20 milliohms = 2V? Likewise for any current from 0A to 12 kA?
3) Then if so, is the converse done in practice? I.e. if you need to know the AFC at a certain point in the circuit, you could load the circuit by 100A or 300A or whatever, measure the resulting upstream voltage drop, compute the source impedance, and then compute the AFC?
Thanks,
Wayne