Source of power for critical loads in hospitals
mshields
Boston, MA
The FGI guidelines and therefore here in MA, the MA DPH requires that critical circuits be fed via a source that is on the same floor. i.e. unlike with Life Safety, you can't go to the floor above or below.
I'm wondering if NFPA 99 and/or NEC 517 mimic this rule. I don't see it. I just want to make sure I'm not missing it.
A client is in a pinch and would like to go to the floor above for 2 critical circuits; adding a new critical panel will require a shut down of the critical riser (or if not a complete shut down at least preparations for that possibility). I just want to make sure I've got all relevant code references.
Much appreciated,
Mike
wbdvt
Rutland, VT, USA
Electrical Engineer, PE
I am not familiar with FGI and looked it up. It appears to be guidelines for design and construction of healthcare facilities. Two thoughts on this and I may be way out to lunch on this but since they are guidelines I don't think they are enforceable unless adopted by the regulatory agency. And design and construction, to me, means more like a new facility.
However having done electrical system studies for arc flash at a number of hospitals, I have only seen the emergency source (diesel generators) either located on ground floor level or out in a separate building. I don't know how you would put a emergency generator on the floor of the critical circuits as there could be many floors involved each with it's own separate source?
wbdvt
Rutland, VT, USA
ok, my terminology for source would be where the power is coming from such as utility source or generator source. So terminology where he means the source of the circuit rather than source of power.
Thank you
gadfly56
New Jersey
Professional Engineer, Fire & Life Safety
Thank you
FWIW, I read that the same as you did until about 3/4 through the OP.
mshields
Boston, MA
to clarify
to clarify
yes - we're talking about source of power; i.e. the panelboard associated with the circuit in question.
As for the FGI guidelines, they are adopted by the MA Department of Public Health such that here in MA, for a hospital, it constitutes a set of requirements rather than what it's name would imply. I believe the Joint Commission and possibly CMS have something to say on the matter; Regardless, here in MA, they are rules not guidelines.
Mike
steve66
Illinois
Engineer
Mike
Illinois has a similar rule which I believe was written and is enforced by the Dept. of Public Health.
Life safety can be up or down a floor, but critical should be on the same floor to make it easier for staff to find and reset breakers.