Spa 680.42.C

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I am really confused about wiring an outdoor spa. Is an insulated equipment ground required from disconnect/gfci/breaker to hot tub?
I understand from panel to exterior of house can be NM but I thought everything was outside required insulated ground?

Also, disconnect is required with in sight. Is there a distance limitation?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Within site means 50' and within sight.

In Sight From (Within Sight From, Within Sight). Where this
Code specifies that one equipment shall be “in sight from,”
“within sight from,” or “within sight of,” and so forth, another
equipment, the specified equipment is to be visible and not
more than 15 m (50 ft) distant from the other.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Once you are on the exterior of the house then you must follow the same rules as a pool so yes an insulated equipment grounding conductor is needed
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you just have a meter on the outside then the issue can be there, or even the meter itself could be an issue. Obviously there is an issue outdoors if the issue is worse in the rain
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
The electrical specifications for the above ground spa state: Heater-4,000 watts "230 volt, 60 amp single phase GFCI protected."
I would think a #6 EGC and 3 -#10s would do the job?
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I apologize for not being more specific. The specification sheet states: 4,000 watts 230 volts. The instruction manual states 60 amps 230 volts single phase GFCI protected. It is a little confusing. I wonder if the 60 amps comes from the fact that spa disconnects are typically 60 amps.
I just assumed the load would be 4000 watts?
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
Thanks for the help. I am still working on this spa. It is an Endless Pools X2000. I don't understand the wiring diagram from the 60 amp GFCI to the spa. It shows two double pole 30 amp breakers and parallel conductors from subpanel to spa. Anyone have any experience with this?
 

Attachments

  • x2000 plan.pdf
    309.6 KB · Views: 9

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Looks like they want you to feed a subpanel (unclear whether they furnish that, sell it, or you provide) with a 60A feed from a 60A, non-GFCI breaker. Then feed two 30A GFCI circuits from the sub to their control box.

I have wired them that required multiple circuits similar to this. Usually (2) 30A and a 20A. They wanted to sell me a subpanel but I provided my own at a much lower cost.
 

kwired

Electron manager
Location
NE Nebraska
Looks like they want you to feed a subpanel (unclear whether they furnish that, sell it, or you provide) with a 60A feed from a 60A, non-GFCI breaker. Then feed two 30A GFCI circuits from the sub to their control box.

I have wired them that required multiple circuits similar to this. Usually (2) 30A and a 20A. They wanted to sell me a subpanel but I provided my own at a much lower cost.
Most cases for me the spa provider already included the disconnect (single breaker or dual breaker as needed) in the sale. I do have to install it though.
 

Beaches EE

Senior Member
Location
NE Florida
Occupation
Electrical Engineer / Facilities Manager
This method helps to reduce GFCI trips due to long runs from the indoor panel to the hot tub and also makes troubleshooting easier by separating the tub electricals into two circuits. I am not sure why they call for a #8 EGC, though.
 

kwired

Electron manager
Location
NE Nebraska
This method helps to reduce GFCI trips due to long runs from the indoor panel to the hot tub and also makes troubleshooting easier by separating the tub electricals into two circuits. I am not sure why they call for a #8 EGC, though.

I think many do that because they have confusion involving equipotential bonding conductors needing to be 8 AWG and they think this means the EGC should be also. But a smaller EGC where NEC otherwise allows is not a problem
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
It is very common to see specifications for equipment state 115 V or 230 V.
Where does this come from? Is this something we just ignore?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
It is very common to see specifications for equipment state 115 V or 230 V.
Where does this come from? Is this something we just ignore?
In the "motor world" they use these numbers universally. So we just know that a 115V will work on our 120V systems and the same with 230V, they will work with 240V. Also you see 460V and that relates to 480V. Most have a tolerance range, that right off I can't remember, but will allow nominal voltages to work with the motors.
 

kwired

Electron manager
Location
NE Nebraska
It is very common to see specifications for equipment state 115 V or 230 V.
Where does this come from? Is this something we just ignore?
AFAIK it is the base that they are designed on, with a tolerance level. Many times you can find no load supply volts up to around 125, which is not quite 10% over that base. Also you will often find as loads get added to the source the voltage will drop some, getting closer to the designed base.

Add enough loads that voltage falls below this base and you are still ok as long as you don't go below designed tolerance.
 
Status