Spa disconnect

Status
Not open for further replies.

nickelec

Senior Member
Location
US
I'm wireing a hot tub for a friend of mine and it's been a while I know for a single family dwelling the emergency disconnect is not required. Do I still need to have a disconnect located within six feet or can I just run my conduit and change over to sealtite before I enter the unit

Sent from my SM-G986U using Tapatalk
 
Last edited:

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
2020 NEC reference 680.13 This image is from 2011 NEC so make sure you update yourself with your regions NEC edition. 1621525900846.png
 
Location
St. Petersburg, FL
Occupation
Electrican
Your GFCI breaker feeding the hot tub needs to be insight of your hot tub and It also needs to be further than 5 ft away from the spas water, it did not sound like the second part was an issue.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Your GFCI breaker feeding the hot tub needs to be insight of your hot tub and It also needs to be further than 5 ft away from the spas water, it did not sound like the second part was an issue.
In almost all cases, when I wire a new spa tub I have the GFCI disconnect (AKA spa panel) located at least 5' away from the edge of the tub and sometimes a few feet more. However, you only need a disconnect means at that location. You can actually have the GFCI breaker in the main circuit breaker panel if you choose to do so. IMHO, I think that wiring method is somewhat of an inconvenience but it is Code compliant.
 