We have a 240V hot tub. Rigid conduit carries 2 hot , 1 N (all #6) and 1ground (#8) from Main to line side of 50A GCFI disconnect located adjacent to spa. Rigid then carries 4 wires on load side to spa. Final 18" of load run is non-metallic liquidtight. The #8 ground wire is bonded to spa ground lug and to GCFI ground lug on the load side, and to the GCFI ground lug and the Main neutral. The main is bonded to the homes iron water pipes.
I've had one inspector tell me to disconnect the ends of the ground wire at the GCFI ground bar and to bond the ground wires together so that the ground is carried directly back to the Main. His reasons that connecting at the CGFI bar allows a ground loop back to the spa through the rigid conduit.
I argue that the terminal run of NM liquidtight eliminates the ground circuit he is concerned about. Would there be any possibility of the buried rigid seeing a ground current?
On a different point, was it necessary to run the #8 ground wire from the Main to the GCFI panel or could the rigid have provided sufficient ground?